I took my own advice and did some pressure testing today. Well... as much as I could.
(Sweeney: BTW My tank is 90% and and temps were in the mid-30's. Same as Seth.)
Despite my testing (results below) I am still confounded as to why my Big Buddy will not work off the side port, using either of the 1 lb connections and the internal regulator, while it will work off the side port using the in-line Mr Heater regulator and the direct (unregulated) QC port.
Presumably, the Mr Heater internal and external regulators are both 11" WC and designed to do exactly the same thing: reduce the full pressure of the propane tank (120-200 psi) down to 0.40 psi. Theoretically, neither configuration should work, since the side port only offers about 20 psi, or only 1/10th what MR heater calls for, as far as input pressures:
View attachment upload_2024-1-1_14-44-2.jpeg
I have no answer as to why Seth's and my workaround works. But it does.
Cary is correct that the CI regulator at the tank offers up slightly more than 20 psi to the rest of the trailer:
View attachment upload_2024-1-1_14-45-0.jpeg
I also corroborated the accuracy of my pressure gauge with another one:
View attachment upload_2024-1-1_14-50-32.jpeg
The pressure at the stove is regulated once more by the 11" WC device which is pictured above in one of Seth's posts:
View attachment upload_2024-1-1_14-46-28.jpeg
This gives us the proper pressure of 0.4 psi for the stove. However the side port is an unregulated line; whatever is being put out the tank and regulator should equal the side port, give or take a couple psi.
Hope this helps someone wrap their head around one of the more esoteric aspects of the trailer. It hasn't exactly helped me come to terms with the inexplicable vagaries of my Big Buddy. But I'll take it.
If I can fix the leak at the crimped connection of the 0-30 variable regulator with gauge (3rd pic down) I may install it permanently in place of the CI OEM regulator. Just so I have another measure of what's going on with the trailer. And something else to keep track of.
Seth: I believe you did. Manually purging a 12 foot hose is quicker, yes. But letting the prime knob do it doesn't take that much longer in time. Maybe 60 seconds at the longest, for me. It helps that when the heater is actually priming/ purging air and fuel is being pushed through the lines, you can actually hear it passing through some of the plumbing in the heater. Whenever I've had what will turn out to be a "no-light" situation... crickets.
(Sweeney: BTW My tank is 90% and and temps were in the mid-30's. Same as Seth.)
Despite my testing (results below) I am still confounded as to why my Big Buddy will not work off the side port, using either of the 1 lb connections and the internal regulator, while it will work off the side port using the in-line Mr Heater regulator and the direct (unregulated) QC port.
Presumably, the Mr Heater internal and external regulators are both 11" WC and designed to do exactly the same thing: reduce the full pressure of the propane tank (120-200 psi) down to 0.40 psi. Theoretically, neither configuration should work, since the side port only offers about 20 psi, or only 1/10th what MR heater calls for, as far as input pressures:
View attachment upload_2024-1-1_14-44-2.jpeg
I have no answer as to why Seth's and my workaround works. But it does.
Cary is correct that the CI regulator at the tank offers up slightly more than 20 psi to the rest of the trailer:
View attachment upload_2024-1-1_14-45-0.jpeg
I also corroborated the accuracy of my pressure gauge with another one:
View attachment upload_2024-1-1_14-50-32.jpeg
The pressure at the stove is regulated once more by the 11" WC device which is pictured above in one of Seth's posts:
View attachment upload_2024-1-1_14-46-28.jpeg
This gives us the proper pressure of 0.4 psi for the stove. However the side port is an unregulated line; whatever is being put out the tank and regulator should equal the side port, give or take a couple psi.
Hope this helps someone wrap their head around one of the more esoteric aspects of the trailer. It hasn't exactly helped me come to terms with the inexplicable vagaries of my Big Buddy. But I'll take it.
If I can fix the leak at the crimped connection of the 0-30 variable regulator with gauge (3rd pic down) I may install it permanently in place of the CI OEM regulator. Just so I have another measure of what's going on with the trailer. And something else to keep track of.
One actual fact: It’s way easier to manually exhaust the air from Mr. Heater’s qd hose. At your own risk! And that’s what nags at me; did I actually get the air out of the straight connection hose when I tested?
Seth: I believe you did. Manually purging a 12 foot hose is quicker, yes. But letting the prime knob do it doesn't take that much longer in time. Maybe 60 seconds at the longest, for me. It helps that when the heater is actually priming/ purging air and fuel is being pushed through the lines, you can actually hear it passing through some of the plumbing in the heater. Whenever I've had what will turn out to be a "no-light" situation... crickets.